I'm a big fan of stern rail mounts. Keeps the tank out in the air where leaks are not so potentially destructive. I have little faith in the venting ability of small hoses, too easily clogged up. We have a 20lb. aluminum tank on the rail and a 10lb. aluminum spare kept in the built in locker the Mk. IIs have, which, on our boat, collects water from I don't know where which is another reason I don't like it. Also don't need to use the solenoid to turn it on and off (amp draw is significant) we just open the valve to use it and shut it when we're done. We have a T on it for the BBQ so no need to waste money and resources on the 1 lb. tanks. This is the 2nd boat we've had this rig on and I wouldn't have it any other way, I actually dismantled the built in setup on both of these boats because I just don't trust it. Our last boat we bought an SS rail mount that cost almost $200, for this boat I built one out of red oak I had around and either tank will fit on it. Cost was pretty much zero.
Bud, are you implying that you have no solenoid in the system??? If that is the case, I strongly (no, make that *very strongly*) urge you to reconsider the set-up. The solenoid isn't there for mere convenience, but rather to save the boat in the event of a galley fire. Amperage is negligible if used as described below - the only current draw is during the use of the stove - but the importance of the solenoid cannot be overstated.
If you or your crew have a galley fire, such as a grease fire due to overheated oil in a skillet, or perhaps the corner of an over mitt gets too near the burner, the VERY FIRST THING to do is to TURN OFF the solenoid switch. This removes the source of the heat, by shutting off the propane at the tank. Only then, do you grab the fire extinguisher and fight the fire.
The skipper and crew need to make solenoid use a habit. Heck, I leave the tank valve ON for days, even weeks at a time; that's no big deal. But when using the stove I and my crew ALWAYS turn the solenoid switch ON, then turn the stove knob ON and light it. Then, immediately after turning the stove OFF, we flip the solenoid switch OFF. Make it a habit.
The Tee for the BBQ is located before the solenoid, therefore the solenoid only interrupts the propane going forward to the galley. The solenoid is not in series with the BBQ. I would vehemently argue that tee'ing into the propane line for the BBQ is much safer than using those 1 lb green propane cans. I consider every one of those cans a bomb-in-training. If stored anywhere within the boat (such as in the cockpit locker or lazarette), a leak in those cheap green cans (caused by corrosion, or manufacturing defect, or mishandling, or...) will allow the propane to find its way to the bilge. I will not allow one of the damn things to be on my boat. Period.
Larry Brandt
S/V High Flight #2109
Pacific Northwest, PDX-based
2002 C-36 mkII SR/FK M35B
Larry, not only am I implying it I am flat out saying I have no solenoid in my LPG system! :-)
I have a manual shut off at the tank, as required by ABYC A-1 standards, specifically ABYC 1.7.3, it goes on to 1.7.6.1.2 as far as valves and tank mounting. Their preferred location for mounting is a place on the exterior of the boat where escaping gases can vent directly overboard. Hard to beat a rail mount for complying with that requirement.
They spend more time talking about venting and especially about locker venting than they do about valves. Clearly, that's the more important issue. I don't like having the propane bottle in an enclosed space, I do not trust those little hoses to vent properly. We all know how those vents get clogged by water, spiders, a myriad of things. That storage locker is fine for storing a tank in with a new style valve but I would not use it with live propane. There is a foot of hose between the tank and the solenoid and if you leave the tank on and that hose developed a leak, well, the vent better work because that hose is live even if the solenoid is off.
It might take a second or two longer for me to reach the valve than the solenoid switch but ultimately, I do believe it is a safer and more reliable system. On our other boat the solenoid valve was seized from corrosion. That's what started this whole thing, that and my already healthy respect for what propane can do, I've seen it first hand. I researched the requirements and spoke to some propane people about this and it seems the best and safest shut off is a hand wheel on a tank that is used regularly. The belief is that solenoids were put in as a convenience item more than for safety.
The shut off is before everything so when it is closed, all the lines out, including the T to the BBQ, are shut off. I would not put a T on the standard system as it came from Catalina.
Our insurance company does not care about solenoids, but they do care about leaving the tank turned on. We are required to turn it off whenever leaving the boat and have developed the habit of turning it off whenever we are not using it. That is the safest system of all, IMHO. Your habit of turning off the solenoid after using the stove is akin to my habit of turning off the tank valve after using the stove.
I think if solenoids were so much of safety thing they'd be required, but they're not and that says a lot. And the false sense of security they instill can be a big problem.
Bud, we'll have to agree to disagree on this one. It seems like neither of us has convinced the other; but I am interested in what others are going to say. Maybe there's something I am not grasping about a possible critical emergency.
At the moment I'll stand by my interpretation, that in the event of a galley fire (let's assume a grease fire...frying oil in a skillet has just flared up) the solenoid is the first tool to use in solving the problem; only then does one reach for the extinguisher. In the case of no solenoid, the first reaction might be to reach for the fire extinguisher instead of accepting the (counter-intuitive) delay of climbing out the companionway, getting to the aft rail and turning off the tank, then returning down a companionway that might by now be dangerous to enter. To use only the extinguisher on the grease fire without removing the heat source doesn't make sense to me...the extinguisher is a one-shot deal.
Larry Brandt
S/V High Flight #2109
Pacific Northwest, PDX-based
2002 C-36 mkII SR/FK M35B
Since references to the ABYC standard A-1 have been made, I draw your attention to the following:
A-1.7.3 A readily accessible manual or electrically
operated (e.g., solenoid) shut-off valve shall be installed in
the low or high-pressure line at the fuel supply. See the
requirements in A-1.7.6.1 for valve location requirements.
A-1.7.3.1 The valve(s) or its control must be operable
from the vicinity of the appliance(s) in the event of a fire at
any appliance(s). If the cylinder shut-off valve is readily
accessible from the vicinity of the appliance, the shut-off
valve on the supply line is not required.
A-1.7.6.1 LPG cylinders, cylinder valves, regulating
equipment, and safety devices shall be readily accessible,
secured for sea conditions, and protected from the weather
and against mechanical damage, and shall be:
A-1.7.6.1.1 installed in a ventilated location on the
exterior of the boat where escaping gases will flow directly
overboard, or,
A-1.7.6.1.2 if the escaping vapors will not flow directly
overboard, the cylinder shall be installed in a dedicated
locker meeting the requirements of A-1.8 LPG
LOCKERS.
These paragraphs are from ABYC A-1 dated July 2006 (the latest according to ABYC web site). If these paragraphs have subsequently been revised to change the intent or content, then I stand corrected.
I suspect the valve on an LPG cylinder (propane tank) mounted on the stern rail does not meet the requirement of A-1.7.3.1 since I don't consider a tank on the stern rail to be in the vicinity of the stove. Further, I don't believe that mounting the tank on the stern rail, with a sunbrella cover on the tank, meets the requirement for protection from weather or [U]mechanical damage[/U] per A-1.7.6.1
The electrical solenoid is held open electrically and is spring loaded closed so there is no electrical draw when shut off. If you consider in the event of a fire at the galley stove, the first reaction, I suspect, would be to grab the nearest fire extinguisher (dry chemical no doubt) and try to put the fire out. Most 5 ABC or 10 ABC dry chemical extinguishers will provide, at best, 10 or 12 seconds of extinguishing agent flow.
Consider what can happen if you abandon the fire for "a few seconds" to try and shut off the propane at the tank on the stern rail and then return to the fire to use the extinguisher. I suspect that it will take more than "a few seconds" to accomplish this, particularly in an emergency. Where as if you have an electrical shut off solenoid on the tank, with the switch in close proximity to the appliance, as required by the ABYC, you would save precious seconds that may help to prevent a fire becoming so large that it results in a total loss, of vessel or life.
Just my humble opinion.
Tom & Janis Grover
C36 #0949
SR/WK, M25XP
Midland, ON
I suppose the design department has been listening, on the 375, there are two built-in gas lockers at the back of the boat. Both drain overboard.
We turn the gas off when we leave the boat.
We also turn the solenoid on and off each time we use the gas stove. Its not that much of a hassle - the power switch is only two steps from the galley. When the switch is on, a red light glows, so is serves as a constant reminder that it is still on.
Cat375 - Rock The Boat - Hull 54
Lake Macquarie - NSW - Australia
Since Larry asked for other comments:
First, I have high regard for both Bud and Larry based upon our dealings and their posting/contributions to our organization. My comments are not meant to take sides.
As for our usage and opinions:
We have the original setup on our boat with one LP tank in the vented locker and a solenoid valve with the switch located on the electrical panel. For better or worse, we have left our manual tank valve open for days at a time while cruising, but ALWAYS open/close the solenoid valve immediately before and immediately after using the stove. I must admit that using the manual valve to stop gas flow at the tank valve probably has a slightly lower risk than using the solenoid valve. The solenoid valve “should” be highly reliable, but is inherently somewhat less so than a manual valve.
In the event of a fire, our plan is to quickly close the solenoid valve, then grab the fire extinguisher we have near the companionway ladder opposite the galley. Personally, I feel better knowing that the solenoid valve has a 99.999% (just a guess) probability of doing the job, and doing it much more quickly than if I had to climb up to the tank.
On those few real long-term cruises we have done so far, we carry a spare 10 lb tank on a cradle made of Starboard mounted to the rail so that a leak would vent overboard. It is therefore somewhat vulnerable to damage, but I believe that to be unlikely. Given that we have only one vented locker, the rail mount seems to be the only other acceptable choice for a spare. I do check the vent in the LP locker regularly and have never found a problem, but I agree with Bud that it is always a possibility.
The potential consequences of a problem with LP are enormous (maybe fatal), so reducing risk is a must, in my view. The reality is that you will NEVER bring the risk of anything to zero, so you do the best you can and live your life.
Cheers,
Duane Ising - Past Commodore (2011-2012)
s/v Diva Di
1999 Catalina 36 Hull #1777
Std rig; wing keel, M35B, Delta (45#)
Punta Gorda, FL
http://www.sailblogs.com/member/diva-di/
Just to add to the discussion.
I also religiously use the solenoid switch before/after each and every use of the stove. The tank valve is opened when arriving at the boat, turned off when leaving. Given the choice, I'd prefer this to having to operate the valve every time.
On my 97 MKII, the propane locker is on the port side aft of the cockpit locker. The lid vents to the cockpit, which is open to the sea via the walkthrough transom. I figure that's ideal for dealing with a propane leak, even if the vent line is clogged; at most, a small amount of propane could be trapped below the tank in the locker itself, anything else would vent out through the lid and overboard.
I also store 2 propane bottles for the BBQ and a small bottle of gasoline for the outboard in the propane locker, above the tank. The lid just closes with that stuff in there and again, if one should leak, fumes would go overboard via the transom.
I'd not like to blow my boat up (or myself) and am pretty comfortable that I've got the propane and gasoline risk minimized. I'd [I][U]never, ever, [/U][/I]have a gasoline inboard engine on a boat. As a kid, I saw a powerboat explode spectacularly off of Cape May Point and burn to the waterline while going out to sea on the tide. I also know someone who had his 40' sport fishing boat explode, throwing him 50 feet from the fly bridge; his wife was hospitalized for 6 months. This [I]after[/I] he had run the blowers for 10 minutes and checked his bilge sniffers. Those two incidents convinced me of the importance of keeping flammables out of the bilge. I had the plastic bowl on the fuel filter of my C30 deform and leak a couple gallons of diesel into the bilge. :eek: I thanked my lucky stars it wasn't a gasoline engine.
Gary and Cathy Price
1997 C36 Mk II Tall Rig/Wing Keel Imagine...
Hull # 1617
Worton Creek, Md.
Northern Chesapeake Bay
Gary, I would bet that your Mk II propane locker has a hose from the bottom that vents to a small thru-hull nearby. You don't have to depend on propane leaks venting into the cockpit at the level of the lid.
Larry Brandt
S/V High Flight #2109
Pacific Northwest, PDX-based
2002 C-36 mkII SR/FK M35B
Yes, it does have the hose. I should have clarified; what I meant was that, at worst, if that vent hose gets clogged by those pesky spiders, the propane locker would vent through the lid and hence, through the transom and overboard. Some propane would redoubtably be trapped below the tank, but if a fire ever got that far, I think that would be the least of your problems.....
Gary and Cathy Price
1997 C36 Mk II Tall Rig/Wing Keel Imagine...
Hull # 1617
Worton Creek, Md.
Northern Chesapeake Bay
I have to agree that Gary's point seems valid. In the event the designed locker vent was plugged, the overflow should vent out through the lid and have little chance of going anywhere but out the open transom.
I love these reasonable discussions. I used to partake in some open forums where 'flaming' each other was rampant. Offering a differing opinion was an act of war in many cases.
Duane Ising - Past Commodore (2011-2012)
s/v Diva Di
1999 Catalina 36 Hull #1777
Std rig; wing keel, M35B, Delta (45#)
Punta Gorda, FL
http://www.sailblogs.com/member/diva-di/
being a musician (amateur), I spend a lot of time at the harmony-central forums. talk about flaming..... And try looking at the responses to an article on CNN. All vestiges of civility seem to go out the window on the internet. This forum is the most civil I've ever seen. To everyone's benefit.
Gary and Cathy Price
1997 C36 Mk II Tall Rig/Wing Keel Imagine...
Hull # 1617
Worton Creek, Md.
Northern Chesapeake Bay
Yes, we will agree to disagree 'cause I still feel safer with this setup.
If I have a fire on the stove the first thing we are going to do is shut the burner off, not go after a solenoid or anything else. I also wouldn't go spraying a fire extinguisher on a grease fire in a pan, which is no doubt the most common stove fire, I'd smother it with a lid as the local fire safety people suggest.
I would not worry about turning the propane supply off before dealing with the fire unless the fire is in some place that it can get to propane supply hose. Hard to imagine that happening in a few seconds the way the hose is run to the stove on our boat. Turning off the propane immediately is one of those generic safety warnings that isn't necessarily the right thing to do in every situation. I was a cop for 22 years, I saw a lot of fires, I guess I don't get excited about stuff when it happens and I certainly don't buy all the safety warnings that are flying around out there as being right for each situation. You react appropriately for the situation you are faced with.
I feel the presence of the controls on the stove make it compliant in spirit if not in exact wording with the section Tom pointed out. You can turn each appliance off right there. The stove is the only appliance we have connected other than the BBQ which is pretty handy to the tank. I suppose I could install a valve in the line somewhere near the stove and make it comply, but then you've just introduced a new point of failure and leakage. Rather have it the way it is. It is after all a guideline, not law.
The only section of those guidelines I feel we might be have a real risk on is the mechanical damage possibility. We have the top of the tank and controls covered with a sunbrella cover and it's hard to imagine what could hit it to damage it. I've thought about making a solid top for it, well vented at the rear, to protect that area. Good winter project maybe.
We had exactly this setup on our last boat which we sold last August and the surveyor had zero issues with it, in fact stated rail mounts are safer than lockers due to the risk of the vent plugging without the owner's knowledge. Had no issue with the lack of a solenoid either.
And finally, as for the reliability of solenoids. The one on our last boat was seized when we bought the boat. It was leaking, so it was open at least to some degree. And the vent from the locker was indeed plugged. Which is that .1% failure that made me decide a solenoid combined with a propane locker was risky business.
I'll give some thought to these comments, perhaps I can install a solenoid in the system where it is now, though I just don't see not having it as a big deal. But there's no way I would ever go back to using the propane locker other than to store a spare tank in.
Flaming is really appropriate given the nature of the discussion wot? Flaming. Get it?
Nyuck-nyuck.
Ah, jeez. Hate to beat this to death, but my good wife just asked me why we don't have to have a shut for the gas supply at the stove in our house. We have propane in our house for the kitchen stove and BBQ. She loves to cook and gas is the serious cook's choice of heat source. We live in the boonies and there is no piped in gas so propane is the only gas source available. We have a 400 lb tank mounted outside the house and plumbed through the house to the kitchen and the front deck.
This was all installed when we built the house in 2001 and it passed all inspections. Insurance company is fine with it.
The only propane shutoff for the stove is behind the stove, you would have to pull the stove out and lean over a counter to reach it. Somewhat risky if there was a fire on the stove, possibly even suicidal. There is another shutoff downstairs in the ceiling somewhere, about 70 feet and 2 flights of stairs from the kitchen. It would be quicker and safer to run outside and turn off the tank. But really, I'd just deal with the fire and not worry about shutting the propane off.
It's kind of hypocritical to suggest that a boat needs to have a master shutoff somewhere at the appliance where it is easily reached when thousands of houses don't have one anywhere reachable. No solenoids here either. Can't remember seeing a fire extinguisher in anyone's house lately either. But it's all necessary on boats.
It seems we can go a little overboard (pardon the pun) with "safety" at times while neglecting it at others. But still, it is a good discussion and I'm certainly reviewing again, for about the 40th time, my decision to go this route. I'm just really struggling with how the solenoid makes much difference to safety. It's handy for sure, but safer?
[QUOTE=bstreet;7054]We had exactly this setup on our last boat which we sold last August and the surveyor had zero issues with it, in fact stated rail mounts are safer than lockers due to the risk of the vent plugging without the owner's knowledge. Had no issue with the lack of a solenoid either.[/quote]
Quite honestly that surveyor was NOT following his own industry guidelines and can put himself at risk doing surveys that way. There are bad, this guy falls into that category IMHO, and good surveyors. A "good" surveyor would have caught that in a split second as a shut off is required near the appliance but not so you'd need to reach over a flame to shut it off.
[QUOTE=bstreet;7054]
It's kind of hypocritical to suggest that a boat needs to have a master shutoff somewhere at the appliance where it is easily reached when thousands of houses don't have one anywhere reachable. No solenoids here either. Can't remember seeing a fire extinguisher in anyone's house lately either. But it's all necessary on boats.
[/QUOTE]
It is not hypocritical it is the standard of practice for marine applications. Houses are different than boats in many regards. Are you using solid copper Romex on your boat? Wire nuts? Brass not bronze or Marelon valves below the water. Most metal in my house is painted steel but on my boat it is 316 SS or bronze to survive the marine environment.
Any good, and I use good carefully, NAMS or SAMS surveyor will flag your system as an "unsafe" installation for an insurance or re-sale survey. Both SAMS and NAMS guys are guided by the ABYC. Solenoids are required equipment for any ABYC builder or boat yard who is an ABYC member and also for surveyors to be guided by.
You can always do what you want on your boat, unless you require an insurance survey by a good surveyor, but to argue that by removing a safety item, you are "safer", is simply an odd argument.
The propane detection systems I install can shut off the solenoid AUTOMATICALLY or manually in the event of LPG bilge fumes. This could be due to a fitting or hose leak or a failure of the stove. Are you standing on your head with your nose in the bilge to monitor it?;)
A well installed solenoid by a careful installer would not have any hose between it and the hard tank piping. Most solenoids I have installed draw roughly .7 - 1 amps. A small dent in the bank during cooking.
Even if my wife and I cooked for four hours per day, never once happened in 20+ years, we'd draw our 375 Ah bank down by just 2.8 Ah's. Usually we are cooking less than 1 hour per day which means less than .7 Ah's..
As for fire extinguishers I have four in my house but I can simply run outside in the event of a fire. On a boat I would need to jump overboard into the ocean. Different safety guidelines for homes and boats which make sense for both applications. Last time I checked my house, and its propane lines, are not subjected to being thrown off ten to 12 foot waves for hours on end...;)
On our old Catalina the LPG locker was on the stern and even if the hose plugged it would have flowed out and right into the ocean as the lid for the LPG locker was on the scoop and below the cockpit floor.
-Maine Sail
https://www.marinehowto.com/
Then this was not well installed. Look at the attached picture, there's at least a foot of rubber in there between the tank and solenoid. That gives me zero confidence. That's what the locker looked like before we bought the boat. Plugged drain vent as well. None of this commented on by the surveyor. Safer than a rail mount and no solenoid? Not in my mind.
BTW, my mention of the amp draw was strictly in passing, it certainly is not a big issue in my decision.
Bud,
Just a couple thoughts, I too have propane as a cooking and heat source at home. The piping in my house is a bit more robust than what is onboard my boat, and even though I live in California my home system is subject to far less movement and vibration. My home is also subject to far less of a corrosive enviroment. Even living near active fault lines I have not felt the need to gimble our stove at home, though earth quake activated shut off valves out side the house are becoming popular and may be required on new structures.
My house does not have a very deep bilge or basement for fume buildup like my boat and most importantly, if I smell a leak at home I can run outside away from danger. My ability to walk on water is no better than my ability to turn water to wine.
[url]http://www.latitude38.com/lectronic/lectronicday.lasso?date=2010-11-10&d...
This guy was lucky.
Cepheus dream
C36 MK I # 825
MK I Tech Editor No Mas
[QUOTE=bstreet;7056]Then this was not well installed. Look at the attached picture, there's at least a foot of rubber in there between the tank and solenoid. That gives me zero confidence. That's what the locker looked like before we bought the boat. Plugged drain vent as well. None of this commented on by the surveyor. Safer than a rail mount and no solenoid? Not in my mind.
BTW, my mention of the amp draw was strictly in passing, it certainly is not a big issue in my decision.[/QUOTE]
As an ABYC member you would not catch me installing ANY hose between the regulator and the solenoid but this is my own perosnal preference and I often go above and beyond the ABYC standards.
That set up meets meets the ABYC standard, because it is all in the locker. I ideally disagree with that type of installation and won't personally do it but builders can because it is inside the locker.. That could be piped to fit it with the solenoid hard piped and I have done it in more cramped lockers than that.
-Maine Sail
https://www.marinehowto.com/
Ditto, my insurance company also insures the boat only on the condition that the propane tank be manually closed when not in use. This is also pretty common practice around here for backyard BBQ's.
As for emergency use of the solenoid switch, the switch is located on the electrical panel in my boat - hardly the most convenient, or obvious place position in case of an emergency.
It really should be located near the galley and prominently labelled.
Graham Mackey
SV Nostromo
1989 C36 908
Tall Rig/Wing Keel
Toronto, Canada
That is an interesting story. That cat exploded, the fire that consumed it was secondary so clearly it was fumes. Webb Chiles reported on one that lifted the deck off a monohull in New Zealand on his blog a month or two ago, but I believe there was no fire in the aftermath. Two guys in the boat got hurt pretty bad as I recall.
It seems to me that most propane incidents on boats that I've heard about are explosions, not fires fed by propane. Maybe a solenoid would have something about that but turning the gas off at the tank certainly would have. Using the setup I have is primarily meant to keep fumes out of the boat, as much as can be done.
Please don't think I am doing this out of ignorance or because I don't respect the dangerous nature of propane, it is exactly the opposite. I do not like propane on a boat, and when we had all the issues with the locker on our first boat I seriously was ready to dump it all and go back to alcohol. We had used an alcohol stove for many years on our powerboat and never once had an issue because we were strict and faithful preheaters. But propane is definitely more convenient and I decided ultimately it was OK as long as it was not stored inside the structure of the boat, anywhere. I still don't like it but aside from eating cold food the options are limited.
Often codified standards, be they laws or just guidelines, are an attempt at addressing as many sins as possible at one shot. The broad brush approach is always favoured by regulators and I speak from experience there, have provided input on drafting several amendments to regulations in this province which is the greatest nanny state in the entire universe. I am trying my damndest to see how a solenoid on our boat, with our specific installation and the way we use it, would add much safety. I certainly feel I am safer than those who leave their tanks on all the time. Clearly our insurance company agrees. Graham's comment about the location of the switch makes a lot of sense, if it's such a big deal safety wise to be able to get to it instantly why isn't it in the galley?
At the moment I am heading back down to the boat to start re-assembling the engine cooling and fuel systems. While there I am going to participate in a new boat olympics event. The companionway cockpit sprint. To see exactly how long it takes to get from galley to tank and close the valve the 2 half turns I open it (I never open a propane bottle more than that, two turns of the wrist). I might set a new world record. Then I'll take some time to see how I might integrate the solenoid into what I have now and secure the whole structure from any mechanical damage. And take a look at implementing Graham's idea of having the switch at the galley. Then will I be OK and not a perceived propane daredevil (who in reality is a propane chicken)?
Meanwhile, two tests. In this test, regularly means every week or two. Now, how many people check their propane locker overboard drain regularly to see that it's clear? Not too many hands going up out there. And secondly, how many regularly test their solenoid to see that it actually is closing when turned off? Hmm, still not too many hands. Wonder who's really safer, me or those who didn't put their hands up? Problem with devices like solenoids and propane lockers is they give you a false sense of security that all is fine and it may well not be.
Bud,
Test how long it takes you to smell a propane leak WITHOUT your head being in the bilge. By the time you smell the propane it is often to late. A propane sniffer/solenoid device will cut the propane supply far faster than any human, who is not laying face down in the bilge 100% of the time.
We ALSO turn the tank valve off after each use BUT we sometimes forget due to HEF (human error factor). Our propane solenoid switch has a big [B][COLOR="Red"][SIZE="5"]RED[/SIZE][/COLOR][/B] LED constantly reminding us the solenoid and PROPANE is ON. We NEVER forget to flip that switch off but have forgotten the tank valve on a number of occasions.
I can't for the life of me figure how you are justifying that the removal of a redundant safety device such as a SHUT OFF solenoid could possibly be safer? Especially with how cautious you appear. There are still plenty of leak points INSIDE your vessel along the hose or the connection to the stove or INSIDE the stove that you may never sniff till it is too late. An automated sniffer/solenoid is far faster and far safer that the human nose on a boat...
-Maine Sail
https://www.marinehowto.com/
Bud,
I have an overboard drain on my propane locker?
You are right I never check it. I have used the propane on my boat three times in four years, have no clue how much is left in the tank as I have not touched it other than to turn it on since purchasing my boat.
Steve
Cepheus dream
C36 MK I # 825
MK I Tech Editor No Mas
[QUOTE=Maine Sail;7061]Bud,
Test how long it takes you to smell a propane leak WITHOUT your head being in the bilge. By the time you smell the propane it is often to late. A propane sniffer/solenoid device will cut the propane supply far faster than any human, who is not laying face down in the bilge 100% of the time.
[/QUOTE]
If I may ask; how reliable are sniffers? Is there a way to test them, eg., sorta like a GFCI breaker?
Not sure if you saw my earlier post about the guy who's powerboat exploded after he'd run the blowers and checked the sniffers; hence the question. I'd love to have something checking the bilge for gas leaks, as you are correct, I never do. The only time I ever remember giving the bilge a sniff was when I arrived at the boat and found I'd left the propane tank on from the prior weekend. I opened all the hatches for about 10 minutes, then went below and checked the bilge. Otherwise, never. Having a sniffer would give me a higher level of confidence, but only if reliable enough to depend on them.
Gary and Cathy Price
1997 C36 Mk II Tall Rig/Wing Keel Imagine...
Hull # 1617
Worton Creek, Md.
Northern Chesapeake Bay
You could easily test a sniffer by discharging a bit of propane near the sniffer. just use a propane blowtorch and don't light it. A little bit of propane will not nuke the boat before the sniffer goes off.
Jason V
Vancouver, BC, Canada
[QUOTE=Nimue;7065]You could easily test a sniffer by discharging a bit of propane near the sniffer. just use a propane blowtorch and don't light it. A little bit of propane will not nuke the boat before the sniffer goes off.[/QUOTE]
I just use a butane lighter stick. They sniff propane and butane. They are fairly reliable but can fail. I keep a spare sensor on-board and test it about every four weeks or so. If you keep a dry bilge they last for a long while but they don't like a damp bilge quite as much..
-Maine Sail
https://www.marinehowto.com/
After seeing all the concern over the LPG internal lockers and detection of gas in the bilge - a thought (rare for me) occurred. What about putting a sensor at the source - In the locker? The monitor I'm looking at can accommodate up to three so my thought was one in the bilge and one in the locker. If the tank, lines or solenoid spring a leak - well you'd know about it before you realized your vents were plugged. Seems a risk for false alarms but maybe worth it?
_____________
Harold Baker
S/V Lucky Duck
Duncan Bay Boat Club
Cheboygan Michigan - Lake Huron